laars endurance ebp
Paul S_3
Paul S_3 Member Posts: 1,294
edited January 2016 in THE MAIN WALL
I have a few customers with this boiler....can anyone further explain the " anti condensing valve" operation to me .....the literature doesnt go too much into detail ...and all of these boilers are not piped primary secondary like the literature shows....thank you Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Aaron_in_Maine
    Aaron_in_Maine Member Posts: 315
    edited January 2016
    The anti condensing valve closes when the boiler might condense and runs the loop in the plate exchanger until the temps comes up. I don't remember the exact temps. It also closes when the flow switch for domestic is activated heating the plate exchanger. Also if the tank sensor says the tank below needs to be heated.
  • lchmb
    lchmb Member Posts: 2,997
    The flow switch likes to stick now and then. If it does the replacement come's outside the cabinet and doesn't see as much heat.
  • Paul S_3
    Ok thanks. ....i have to keep the acv manually opened for the customer to get heat....it seems like the boiler control does not power acv....once the tank meets temp ....and im not getting 24v at the t & t terminals that go to the HEATING zone valve end switches....paul s
    347-692-4777
    ASMHVACNYC.COM
    Aaron_in_Maine
  • Paul S_3
    Could the boiler control be at fault? Paul S
    347-692-4777
    ASMHVACNYC.COM
  • Aaron_in_Maine
    Could be the control. Check for continuity at the domestic flow switch to make sure it's not sticking. If it's the old style that sits on top of the plate exchanger somtimes you can take it out and clean it.