Triangle Tube Excellence Problem
Paul Pollets
Paul Pollets Member Posts: 3,671
I installed a TT Excellence 110 about 5 years ago that uses 12 wall panel radiators and of course, provides DHW. The CW feed is manual and the boiler drops to zero pressure with 4 hrs. of filling to 15PSI. There are no obvious leaks on the system or underneath the boiler or "near-boiler" piping. The system starts up immediately after re-filling. The boiler relief valve was replaced yesterday. Anybody have some ideas?
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,584
    Pinhole in a tube? Goes right out the condensate drain unnoticed. Had a Solo 110 with that once.
    GordySteve Minnichrick in Alaska
  • Paul Pollets
    The expansion tank is fully charged and not leaking.
    Robert, How would one tell if there's a pinhole in the firetube HX?
  • Aaron_in_Maine
    Aaron_in_Maine Member Posts: 315
    You could pull off the condensate trap with the unit off and see if it's dripping a lot of water. If you are losing that much water you will see it.
    kcopp
  • Tom_133
    Tom_133 Member Posts: 961
    Isolate, drain boiler and air test for an hour + or -. You may want to remove and plug relief valve hole, then test to 50psi
    Tom
    Montpelier Vt
  • Paul Pollets
    I went back last night and there was no condensate at high temp. Looked further and there was a small leak at union nut(s) on thermostatic anti-scald valve and a tiny pinhole leak at solder joint under union nuts.
  • SWEI
    SWEI Member Posts: 7,348
    Good catch.
    For the few (older) systems that actually require an auto feeder, we still try to avoid leaving them on 100% of the time. The laying of even fractionally educated human eyes on a system every month or so has some real value.