Triangle Tube Excellence Problem
Paul Pollets
Member Posts: 3,665
I installed a TT Excellence 110 about 5 years ago that uses 12 wall panel radiators and of course, provides DHW. The CW feed is manual and the boiler drops to zero pressure with 4 hrs. of filling to 15PSI. There are no obvious leaks on the system or underneath the boiler or "near-boiler" piping. The system starts up immediately after re-filling. The boiler relief valve was replaced yesterday. Anybody have some ideas?
0
Comments
-
Pinhole in a tube? Goes right out the condensate drain unnoticed. Had a Solo 110 with that once.To learn more about this professional, click here to visit their ad in Find A Contractor.3
-
The expansion tank is fully charged and not leaking.
Robert, How would one tell if there's a pinhole in the firetube HX?0 -
-
Isolate, drain boiler and air test for an hour + or -. You may want to remove and plug relief valve hole, then test to 50psiTom
Montpelier Vt0 -
I went back last night and there was no condensate at high temp. Looked further and there was a small leak at union nut(s) on thermostatic anti-scald valve and a tiny pinhole leak at solder joint under union nuts.0
-
Good catch.
For the few (older) systems that actually require an auto feeder, we still try to avoid leaving them on 100% of the time. The laying of even fractionally educated human eyes on a system every month or so has some real value.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements