Correcting Main Vents

tginnj
tginnj Member Posts: 2
I'm looking to correct a main vent issue on my system. There is currently one small vent at the main's connection to the return on each main. This vent (see first picture) sits on a 1/4 nipple and a hodgepodge of bushings and couplers.

Each main is 30 feet long, 2" pipe. Reading through other posts on this forum, it seems as though two Gorton #1 vents per main should be sufficient. Do I need more than two per main? There are plugged tees (see second picture) about 18-24" from the end of each main that I thought would be an ideal place for the new main vents on an antler.

I think the plugs were originally installed in '95, when the entire system was split into two separate systems. It's a two family, so one of the previous owners separated the second floor from the first floor around that time. How should I tackle removing those plugs? They're 1 1/2", so I'm not sure what size pipe wrench I should be using. Since they've been sitting so long and have also been painted, I was going to clean up the visible threads with a pick and hit them with some PB Blaster before attempting to remove.

Also, What's the best way to attach the antler at those locations so it's sitting vertical?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,883
    At 30' you should do at least 3 #1 vents or a single #2 possibly more depending on system performance. The location at the end is your best bet IMHO.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • tginnj
    tginnj Member Posts: 2
    Is connecting the main vent antler to a single 1/4 nipple going to have sufficient air flow for the new vents? I'm all for not having to screw around with those tees if possible.
  • KC_Jones
    KC_Jones Member Posts: 5,883
    1/8" pipe flows enough to support a single #2 vent or 3 #1 vents so if you have 1/4" pipe you should be totally fine and actually have a bit of cushion.