Member Posts: 2
I'm looking to correct a main vent issue on my system. There is currently one small vent at the main's connection to the return on each main. This vent (see first picture) sits on a 1/4 nipple and a hodgepodge of bushings and couplers.
Each main is 30 feet long, 2" pipe. Reading through other posts on this forum, it seems as though two Gorton #1 vents per main should be sufficient. Do I need more than two per main? There are plugged tees (see second picture) about 18-24" from the end of each main that I thought would be an ideal place for the new main vents on an antler.
I think the plugs were originally installed in '95, when the entire system was split into two separate systems. It's a two family, so one of the previous owners separated the second floor from the first floor around that time. How should I tackle removing those plugs? They're 1 1/2", so I'm not sure what size pipe wrench I should be using. Since they've been sitting so long and have also been painted, I was going to clean up the visible threads with a pick and hit them with some PB Blaster before attempting to remove.
Also, What's the best way to attach the antler at those locations so it's sitting vertical?
Each main is 30 feet long, 2" pipe. Reading through other posts on this forum, it seems as though two Gorton #1 vents per main should be sufficient. Do I need more than two per main? There are plugged tees (see second picture) about 18-24" from the end of each main that I thought would be an ideal place for the new main vents on an antler.
I think the plugs were originally installed in '95, when the entire system was split into two separate systems. It's a two family, so one of the previous owners separated the second floor from the first floor around that time. How should I tackle removing those plugs? They're 1 1/2", so I'm not sure what size pipe wrench I should be using. Since they've been sitting so long and have also been painted, I was going to clean up the visible threads with a pick and hit them with some PB Blaster before attempting to remove.
Also, What's the best way to attach the antler at those locations so it's sitting vertical?
0
Comments
-
At 30' you should do at least 3 #1 vents or a single #2 possibly more depending on system performance. The location at the end is your best bet IMHO.0
-
Is connecting the main vent antler to a single 1/4 nipple going to have sufficient air flow for the new vents? I'm all for not having to screw around with those tees if possible.0
-
1/8" pipe flows enough to support a single #2 vent or 3 #1 vents so if you have 1/4" pipe you should be totally fine and actually have a bit of cushion.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements