quiet zone valve for point of use electronic thermostat

So I'm looking for a quiet 1/2" or 3/4" zone valve. One that can not be heard when actuating in the same room at night.
It would also be ideal if it did NOT require a holding current to remain open. This would mean it was a stop and stay put type. I guess this would need at least 3 wires (common, open, close). With this it would also be possible implement variable flow - which is the best solution. If it was a stop and stay put, then it wouldn't need to be so quiet.
Thank you!
Chris
Comments
-
How do you plan to control the variable flow?0
-
So the valve will be in each room and not the equipment room?0
-
Thermo-actuators type zone valves are silent, the low current draw 250 mA for a few seconds at start up, then require a small holding current.
Most any zone valve that involves a motor and gear train, or spring return will make some noise.
If you want wireless, variable flow type, sounds like a thermostatic radiator valve is what you are looking for?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I think Heatlink sells a modulating thermal actuator zone control.0
-
I found a 3/4" Straight Zone Valve and the thermal actuator that controls it. It seems like it would be as quiet as possible! However, the thermal actuator consumes a lot of power to remain open so I don't think it would work for me in a retrofit application. Do you know if there is a mechanical version that can move and remain at the position?SWEI said:I think Heatlink sells a modulating thermal actuator zone control.
0 -
Could you point me to one?hot rod said:Thermo-actuators type zone valves are silent, the low current draw 250 mA for a few seconds at start up, then require a small holding current.
Agreed. However, it is my hope that someone makes one the moves slow enough that it is quiet enough....hot rod said:Most any zone valve that involves a motor and gear train, or spring return will make some noise.
I found Honeywell Braukmann T104A1040 I wasn't aware they worked with water loops. If I can't find an electronic one then I might end up going in this direction.hot rod said:If you want wireless, variable flow type, sounds like a thermostatic radiator valve is what you are looking for?
0 -
Here are some choices. Disclaimer: I do work for Caleffi.
The two thermal actuator versions we offer are the unique TwisTop, which allow manual operation. Also a low current draw version 6763, non TwisTop..
Here is a graph that shows power consumption. Notice the thermal type only pull a high draw for less than one minute.
Sorry the 6763 low current is not on this graph yet, it will be in the middle of the chart with a 6VA inrush, 3W holding.
A motorized ball valve, red line on bottom drops power when open, or closed but it does have a small amount of motor and gear noise. It also requires power to open and power to close, 3 wire.
Notice also we offer these valves with press fittings for ease of installation.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thank you all - I learned enough keywords to find what I was after. A 'floating control' actuator with a push type 'valve body'. Turns out I was seeing them but didn't make the connection or thought they're for steam....
This site had a very useful detailed explanation of the control terms:
http://controltrends.org/commercial-hvac/03/understanding-onoff-floating-modulatingproportional-control/0 -
a0
-
Hot rod, thank you for the detail. I think the *floating* motorized ball valve is likely the best choice. For this I should only need to nudge the valve a bit periodically and otherwise it takes no power. I can't seem to find one from Caleffi (at least at my online supplier). Do you know of one? For comparison, the Erie AT33A000 seems like the best choose - but I don't know how much noise it makes.0
-
Belimo is a good source also. Select a valve, then add an actuator. You may need to contact a rep or factory support as the catalog has an overwhelming amount of choices.brainfog said:Hot rod, thank you for the detail. I think the *floating* motorized ball valve is likely the best choice. For this I should only need to nudge the valve a bit periodically and otherwise it takes no power. I can't seem to find one from Caleffi (at least at my online supplier). Do you know of one? For comparison, the Erie AT33A000 seems like the best choose - but I don't know how much noise it makes.
Belimo is heavy on tech info, support, and engineering. I'd guess they test controls in a quiet room like many of the major pump manufacturers do. Let them know of you noise concerns when you call them.
http://www.belimo.us/americas/
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Belimo CCV, though you do need do size them correctly. What's the design flow rate for each zone?brainfog said:
At smaller sizes (characterized Cv up to 14) the TR24 actuators draw about 1VA when running and zero (or nearly so) when stopped (in position. ) The -SR versions accept 2-10V inputs and the -3 versions work with floating inputs (energize one terminal to open or the other to close.)0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 424 Carbon Monoxide Awareness
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 954 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements