Pressure excedance ??
rodjburge
Member Posts: 2
I just recently bought a house with a water boiler heating system. In turning it on it seems to be working OK but the pressure gauge on the system is pegging out at 30+. With the system off, the gauge reads around 12 psi. A couple of questions......
1) Am I in danger of blowing the system or does the relief valve give me the needed safety factor.
2) With the system off, should it maintain the 12 psi head pressure ?? I am assuming a non-functioning pressure gauge.
Thanx All
Thanx All
Is a tankless coil or indirect hot water heater connected to the boiler?0
At 30+ is your relief valve opening? If it's rated at 30, and most of them are, it should be opening at 30.Steve Minnich0
Response to the above inputs.......
Not sure that I know the diff between tankless and indirect. The system is one unit that has a pilot/burner. It is obviously coming on and heating the water that appears to be contained in a tank with the pipes for the flow running through out the house.
There is not relief valve opening. If it wasn't for seeing the gauge pegged I would assume that all is running properly.0 -
Do you have a separate water heater for your faucet hot water?
If your heating boiler is at 12 PSI when cool and rises quickly when the heat comes on, then you have no air in your expansion tank and should not use the heating boiler until you get it fixed. The relief valve may be stuck or someone may have put a plug in it because it was dripping.
Post some pictures of your boiler and any tank attached to it.
You mentioned a pilot light, if your system is older it may have a tank hanging above it at the ceiling. DO NOT continue to use this until you get it fixed. Someone here may help you if we have pictures.0 -
It may just be a wonky gauge but you should have it looked at NOW.
3PSI gauge0
- 87K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 109 Geothermal
- 161 Indoor-Air Quality
- 994 Plumbing
- 391 Solar
- 55 Water Quality
