Carlin EZ gas numbers
Options
kcopp
Member Posts: 4,614
in Gas Heating
I installed a new Steam boiler today. Nat gas... Peerless WBV w/ a Carlin ez.
I set the air shutter to 20% as the factory specs directed me to start w/ .
I had a dickens of a time to get the numbers to come into spec.
I had the shutter practically closed.
ended up w/ stack of 266F
O2 2.7%
CO2 10.2
Eff 85.6%
CO 106ppm
EA 15%
EA I thought was supposed to be in the 25-30% range.
Any thoughts?
I set the air shutter to 20% as the factory specs directed me to start w/ .
I had a dickens of a time to get the numbers to come into spec.
I had the shutter practically closed.
ended up w/ stack of 266F
O2 2.7%
CO2 10.2
Eff 85.6%
CO 106ppm
EA 15%
EA I thought was supposed to be in the 25-30% range.
Any thoughts?
0
Comments
-
Check your orifice size, manifold pressure and input rate. Sounds like it's underfired.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Orifice nipple was drilled out to 7/32"
Clocked the meter to 119k btu.
I attempted to check the manifold pressure but I couldnt get the 1/8" hose adapter fitting to screw in smooth.
0 -
Which WBV?
The meter may be reading wrong- we've seen a few. Manifold pressure will help us get to the bottom of this.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 428 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements