short cycling
What is the water temperature doing throughout this cycle? Also what kind of aquastat is on the boiler and what is the LL (low limit) setting.
Are you using deep set backs? If so, it's probably acting correctly (not ideally) if it's coming up to temperature (high limit), shutting off burner, but letting circulator run until the water temperature drops, the firing the burner to raise the tempature....over and over.
Everytime the circulator comes on in this high water volume system, lots of cold water come back to the boiler, stopping the circulator.
Could still be air, could be the circulator is not working, or the control not turning the circulator on...could also be the new thermostats aren't set up correctly.There was an error rendering this rich post.
I agree,STEVEusaPA said:What is the water temperature doing throughout this cycle? Also what kind of aquastat is on the boiler and what is the LL (low limit) setting.
The circulator should be running continuously, it sounds like it is turning off with the boiler call."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Might sound crazy, but did you change the thermostat with the new install? Is it possible the CPH setting is incorrect? If it's set for forced air this sounds like the type of thing it would try and do, run as much as 6 times over the course of an hour to get the room to temperature....if it's a digital thermostat anyway.0