i have an old Hoffman number 15 vacuum valve leaking steam
what can i put in place having trouble finding replacement???
  • JUGHNE
    JUGHNE Member Posts: 11,063
    Is this a steam main vacuum/air vent?
    Do you still have a true vacuum system, or is this left over from coal burning and you now have a gas or oil burner?
    PaulStraface_2
    Steamhead Member Posts: 16,861
    This is probably mounted on a dry (overhead) return near a Differential Loop, on a Hoffman Vapor system. If there's steam in that dry return, one or more traps need to be repaired.
    For a replacement, I'd use one or more Gorton #2 vents.
    Consulting
    PaulStraface_2
  • PaulStraface_2
    PaulStraface_2 Member Posts: 5
    thank you for the advise. yes it is on the dry return and it is not a vacuum system any more has a vapor stat running at 8 oz. We are replacing 7 bad traps as well. There was coal at one point because there was an old coal shoot in the basement but gas now.
    Don't forget the "crossover" traps at the ends of the steam mains.
    Consulting