Chamber condition
Video:
http://youtu.be/cIAab0-MHwsThanks.
Looks typical, looks like the bottom needs a vac. But a gentle vac, bc the rug could come up in chunks too. Target wall looks ok, front plate refractory seems solid looking. Swing door refractory as well. The end cone protector is a little tattered. When it's fired, the overall condition can be better observed. I loved the Starfire 3's. Predictable, clean running, perfect pressure drop thru HX.0
If I sold oil, I'd really love Starfires! High stack temps!
The 3-section Starfire has higher stack temps than the larger ones. They run nicely with Carlin EZ-Gas burners too!All Steamed Up, Inc.
Consulting2 -
What relays did you use?All Steamed Up, Inc.
Consulting0 -
OK- so do those zone purge relays continue to feed power to the circs after the zone thermostat drops out the usual zone relay, stopping the burner and (if the purge relay weren't there) the circ?
If so, I've been looking for something like that.All Steamed Up, Inc.
Consulting0 -
You're not the only one,yet no manufacturer sees the opportunity?Steamhead said:OK- so do those zone purge relays continue to feed power to the circs after the zone thermostat drops out the usual zone relay, stopping the burner and (if the purge relay weren't there) the circ?
If so, I've been looking for something like that.0 -
Non proprietary. How hard would it be to put an adjustable circ or ZV off delay on every control?Hatterasguy said:EK definitely saw the opportunity and has capitalized on it IMHO.
Have to use off the shelf stuff, can't create something that no one can service or understand.Hatterasguy said:Not very difficult at all.
In fact, if I were to start this system from scratch, I could eliminate all the Taco 501's and just use a transformer and the Elko off time relays. The package would be less costly and about 1/2 the current size.
You might consider it for your oil conversions.
2 -
I could tell stories..........Hatterasguy said:Ahh...........it's not exactly rocket science.
I'm sure you could service it with ease.
Now, the oil companies................
Not sure how this one will fare in that regard. Will probably have to help them if they get in trouble with it as the control strategy is completely different.