Happened more than once.
Member Posts: 4,385
Replaced an expansion tank and the pressure goes up on a call for heat. It's as though the system doesn't see the new expansion tank.
Is the tank sized correctly? Never assume that what was there was correct. Also I have seen feeders go bad when the water is turned off and then back on and slowly creep increasing the pressure slowly.0
I replaced it with the same size x-tank because it was large enough.
The pressure only goes up when its heating which should rule out a problem with the fill valve, no? This did come to mind, though and I was going to turn off the city water as a test.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
This may be a stupid question but, how can the pressure go up if the tank is working correctly? It's impossible, no?
Get a dead tank out of the box? I've had it happen. ..0
I agree. The possibilities are as follows: the connection from the tank to the system is blocked, the tank is under sized, the tank is not properly set to system pressure prior to installation, or the tank is defective. If none of the above are true then the pressure will not go up.0
Is this CI radiation?0
I was going to ask where I could get one of those tanks.
From my experiences.....the pressure will always slowly build, and stop below the point at which the PRV discharges, as long as the tank is sized correctly and everything is working correctly.0 -
Well okay, I didn't mean that it would not go up at all, It will always go up, just within the bounds of normal parameters. I typicallay do not see an increase of more than 5 psi from cold start to operating temperature if everything is sized correctly. Occasionally more, but if you set your static fill pressure to 12-15 psi for the average residential system, I would not expect the pressure to go up to more than 20 psi. I should have been more clear, my apologies.
@Paul: they are magical tanks, you have to pay extra for the little gnome to carry the small buckets of water to the nether dimensions and back as the water expands and contracts! They are made by the same people that make the magic smoke that electrical motors and transformers run on. Contrarty to popular belief the electricity is what keeps the smoke in.
JUGHNE may be on to something, I have seen high mass systems like CI radiators or large thick radiant slabs have higher expansion tank requirements than I anticipated, due to the large thermal mass of the system. Although if someone would like to elaborate on the physics of that phenomoenon I would be interested.
I feel like it is because the extra thermal mass acts as if it were another heat source and there are times when the mass is up to temperature and is dumping heat into the system water, at the same time as the boiler, thus making the water see more of a heat source than just the boiler, necessitating a larger expansion tank. I have never actually looked this up however and I would love to get a definitive answer!
just curious. I have had a couple of old system retrofits with CI rads and one radiant floor that was steel pipe in the concrete. I must have mis calculated the volume. I know the system cant heat over the boiler, just thought maybe there was a total excess of heat at some point, but then again, all the btus ultimately came from the boiler to begin with...hence the question. It is pretty rare that I run into that problem and increasing the size of the tank always solves the problem. Thanks for the clarification!
I am in Colorado, so our smoke is pretty magical1 -
Thanks!0
The CI rads inquiry was because some 2nd floor rads not completely bled of air can constitute additional air cushion.
In one case it was the only air cushion and when the air was bled later in the season the PRV would open.
I'm caretaker of boiler systems for a church, the Rectory house is not lived in. Only used as day time office. The second floor rads are not bled completely for the reason of not heating that floor. Just maintain water movement along the lower sections.0 -
Thanks, guys. I like Hot Rod's suggestion that the bladder might be stuck. I remember when the system was fully pressurized and I opened the ball valve at the expansion tank, there was no sound. I'm going back on Tuesday and will fiddle with the pressure.
xxoo
Two btu per sq ft for degree difference for a slab1 -
Several years ago ME broached the subject as he has had it happen more than once. I believe what he stated doing was adapting a Schrader valve to the tank inlet and putting air pressure into the water chamber until it broke free. You might want to PM him.Thanks, guys. I like Hot Rod's suggestion that the bladder might be stuck. I remember when the system was fully pressurized and I opened the ball valve at the expansion tank, there was no sound. I'm going back on Tuesday and will fiddle with the pressure.
xxoo0 -
The butyl have a wrinkle and got stuck?0
- 86.8K THE MAIN WALL
- 56 Biomass
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 69 Pipe Deterioration
- 962 Plumbing
- 385 Solar
- 15.3K Strictly Steam