Any comments appreciated
Santilal
Member Posts: 42
Hi
I have been pondering on how to fix a number of design and installation errors that exist in the heating system installed in our new home a few years back. It still works, but has a number of querks. So I have come up with a new design (attached) and I would appreciate any comments about it.
I have tried to provide adequate hydraulic separation (previous design had none). I also have provided for boiler low temperature protection, and I am toggling the in-slab with the DWH because the installer thinks that there is not enough flow to supply everything at once. There will always be an open flow path for P2 - even if all of the TRV's are closed, there will be a path through the DWH or the inslab system. In the existing design P2 can become dead-headed. I have tried to keep the number of circulators to a minimum to lower the operating electricity costs.
There are 6 inslab circuits and 12 radiators. I hope I have provided enough info for you experts, but I am happy to provide any additional info.
Thanks.
Santilal
Thanks.
Santilal
One expansion tank suffices. With TRVs why do you need zone valves? I haven't seen them in use but seems to me that those new intelligent circ pumps are better than zone valves.0
Hi
Thanks for the comment. The reason for the zone valve on the radiator circuit is because it already exists. I agree that it isn't required, but as it is already there I thought I would leave it. The other two zone valves are required because I need to select the priority water heating load or the in-slab heating. The installer thinks that there is not enough flow available to run both together, but I am not really sure.
The original install had several other design flaws which I am trying to resolve with this design. One issue was that the circ was dead-headed when all TRV's were off. Another issue was that the boiler loop and the distribution loop were not correctly decoupled.
Thanks.
Santilal0
- 121 Chimneys & Flues
- 15.8K Strictly Steam