5 year old geothermal system water wil not shut off after heating cycle
        
            Options        
            
        
                
                    thedealmakinman                
                
                    Member Posts: 1                
            
                        
                
                                    
                                  in Geothermal             
            
                    I just discovered the water runs continuously after a heat cycle.  if I turn geo off the water will turn off normally. when turned back on the water will ramp up normally in about 1 minute, then the geo fires up about 4 minutes later.  BUT, when cycle is finished the geo shuts down normal, and the water continues to flow.  My light bill last month was $400!  I suspect the taco valve on the incoming water supply.  Any suggestions?                
                0                
            Comments
- 
            Yes seems like your Taco won't close, pull off the top-most wire and make sure it's not a control issue.
Gary0 - 
            Sound like a control issue if the valve closes after you turn the power off. Try taking the wires off the valve and see if the valve closes . If it does you must be getting voltage from the board in the heat pump and the valve is good. Remember that the TACO valves are a slow closing type of valve so it will take awhile .0
 - 
            If you need assistance with a control I would be happy to help. HBX does offer a geothermal control and a zone module which can control when your equipment is on or off and for how long.Comfort
Control
Innovation0 
Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements
 