one or two pipe system
lee.h
Member Posts: 1
in Oil Heating
hi all,
just bought a Worcester heatslave combi 18/25 and was wondering if I have to fit a one or two pipe oil feed system as the oil tank is probably 1 meter below burner level.
Lee
just bought a Worcester heatslave combi 18/25 and was wondering if I have to fit a one or two pipe oil feed system as the oil tank is probably 1 meter below burner level.
Lee
0
Comments
-
You need a 2-pipe system if the tank is below the burner,
Unless you use a Tigerloop. Then, you can do it with one pipe. I'd use the Tigerloop.0