Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
one or two pipe system
Options
lee.h
Member Posts: 1
in Oil Heating
hi all,
just bought a Worcester heatslave combi 18/25 and was wondering if I have to fit a one or two pipe oil feed system as the oil tank is probably 1 meter below burner level.
Lee
just bought a Worcester heatslave combi 18/25 and was wondering if I have to fit a one or two pipe oil feed system as the oil tank is probably 1 meter below burner level.
Lee
0
Comments
-
You need a 2-pipe system if the tank is below the burner,
Unless you use a Tigerloop. Then, you can do it with one pipe. I'd use the Tigerloop.0
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 986 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements