on sizing: increasing EDR for third floor apartment in one pipe steam system
timmckenna
timmckenna Member Posts: 3
edited March 2015 in Strictly Steam
Hi,
I know that typically there is a 1.33 factor figured in for piping. What would be a good factor in the case where the new boiler is serving a third floor apartment? Compared to an apartment on the first floor, there are 7, 1 or 1-1/4 ~20', pipes (~ 140 more feet) running through the walls of other apartments to supply the 8 third floor radiators. EDR = 261, radiator load 62,500 BtuH
(thanks fred, sorry I was unclear)
  • Fred
    Fred Member Posts: 8,542
    For starters, There is no way one 1" pipe will supply 8 radiators totaling 261EDR, especially running 140 feet. We are talking steam right? Is this a 1 pipe or 2 pipe system? Either way, I can't see it happening.
  • timmckenna
    No you are right. There are 7, ~20' 1" pipes running up from the basement through the walls of lower floor apartments. It is possible they are 1 -1/4 . I'll have to check
    Jamie Hall Member Posts: 26,839
    I hope it is two pipe... or at least 1 14... the 1inch risers are marginal for one pipe. Watch your pitch on any horizontal runouts or it will hammer.
    However, to the question: The normal pickup factor will be fine.
  • Fred
    That makes me feel better. Is this a 1 pipe steam system (Only 1 pipe on each radiator, with a valve on it and a vent on the other side of the radiator)? I hope those pipes are 1-1/4" That would make me feel better too. In any case, as Jamie already said, you don't need to add anything to the boiler for additional Pick-up. It will be fine.
  • Fred
    Also, be aware that you don't need to add any pick-up factor to the boiler when sizing it. The manufacturer has already built that into the boiler. Just use the Sq. Ft. Steam rating on the boiler plate and match that , as closely as possible to your total radiator EDR.
  • timmckenna
    Yes, the tables are pretty clear for Utica, Peerless and Burnham. Problem is the supply house guy is telling my plumber that I need a 150,000 BTU/hr for boiler since it is on the third floor. I could see adding a little to the 1.33 but what they want to sell me seems crazy.
  • Fred
    No, you don't size a boiler based on the number of floors. You size it based on Total EDR. That guy doesn't know what he is talking about.
  • KC_Jones
    KC_Jones Member Posts: 5,907
    You would be massively oversized at 150k. You only need around a 100k input boiler for 261 sq ft. A 150k boiler would probably short cycle like mad. Don't do it for sure.
    2014 Weil Mclain EG-40
    That plumber is bats. Suggest he stick to installing faucets. Steam doesn't care what floor it's on. It's all in the EDR. Match that, and your good to go.
    EBEBRATT-Ed Member Posts: 19,598
    OMG. Another one that thinks you have to "lift" the steam because it's the third floor.
    I tell my students with hot water closed loop 5 story building that the pump only overcomes the resistance of the system, pipe, fittings etc That if I pushed the building on it's side and it was laying down and was now only two stories tall I could use the same pump. I get the deer in the headlights look.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    The game is over because the boiler cannot take the pressure; however if the boiler is removed, and the pump is just on a vertical loop, it can still circulate the water, (with some friction loss due to loop length).--NBC
    I was only talking about using the same pump, same head, same gpm didn't mention the boiler. I know the static pressure will change. The resistance of the system (pipe, valves, fittings) stays the same weather the building is vertical or horizontal so the pump capacity (head & gpm) remain the same. That was my point in a closed loop you don't "lift" the water you only overcome the systems resistance.