hot surface ignitor
Paul S_3
Member Posts: 1,292
in Gas Heating
Not sensing flame.boiler is a blue jacket weil mclain he ii .....I ohm out Hot surface ignitor and I get 120 ohms....If there'sa problem with the ignitor how doi check?thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
What is the Model number of the boiler and does it have an integrated boiler control? If so what is the make and model. Then I will be able to answer your question. If it does have a boiler control are any lights flashing?0
Weil mclain he 11-6.....boiler integrated control 1013-200.....my problem is that the gas valve will no open im getting 17 volts to all low voltage safeties to ground I'm getting 17 volts to gas valve to .....t - former is getting at primary 120 secondary is getting 28 v to integrated control coming out of control is 17 volts ....I grounded gas valve etc Paul sASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Will the valve open if you give it direct 24 volts? Test this with gas shut off and listen for the audible click of the solenoid in the valve. Do a step by step test of the nine pin connector, if that is difficult for you to follow I can send you by e-mail the procedure. My e-mail address is gastc@cox.net.0