80% trane furnace runs than on shut down it reignites the burner for a few seconds
mburg
mburg Member Posts: 48
I have a customer who has a 80% trane furnace it will run and heat the house but after the burner shuts down it will reignite the burner for a few seconds than shut down again. I have replaced the thermostat that didn't help. Any thoughts on what it could be?
  • Ironman
    Ironman Member Posts: 7,730
    Could it be cycling off on high limit and then back on before satisfying the thermostat?
    Bob Boan
  • mburg
    That's definitely a thought I checked the temperature rise and it was within the specs so I didn't think anything of it.
  • icesailor
    icesailor Member Posts: 7,260
    Is it the burner and fan coming on or just the fan? Doesn't the fan keep running after the burner shuts off on a satisfied call but the fan continues to run? Because of residual HX heat?
    Is the return big enough to give satisfactory air flow through the return? Is it a system with 100,000 worth of output air with a return of 8" round flex duct? I've seen that.
  • mburg
    The burner shuts off the fan stays running because of residual heat than the burner turns on again a few seconds after the burner originally shut off runs both the fan and burner for a few seconds than the burner shuts off and the fan runs until the hx cools and shuts off
  • JUGHNE
    JUGHNE Member Posts: 11,460
    That used to be a symptom of heat anticipator problem in old T-stats. But you said you changed the T-stat. Is this upflow or downflow, some downflow had fan control problems.
  • mburg
    Yeah the heat anticipator was my first thought that's why I changed the stat, but it didn't help. It's upflow
  • GW
    GW Member Posts: 5,065
    are you positive the flame is going to all the burners right away??
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • wogpa67
    wogpa67 Member Posts: 238
    like ironman and gw stated it may be bouncing off of the hi limit. what type of air filter is on this furnace?
  • DZoro
    DZoro Member Posts: 1,048
    How old of a unit?
    Supply and returns appropriate for the furnace? If so, high limit, and don't forget to check HE, crack is possible cause
  • mburg
    I couldn't get it to do it when I was there but these are definitely some good ideas, I'm gonna spend some more time with it. Thanks for the ideas!