vent-rite No 1 adjust vs gorton
on a setting of 1 on the vent rite, what would that roughly equal on gorton? and a setting of 8 would roughly equal what on gorton size?
  • BobC
    BobC Member Posts: 5,539
    A Gorton #4 is 0.025, Ventrite at 1 is 0.033, Gorton #5 is 0.080
    The Ventrite at 8 is 0.083 about the same as a Gorton #5
    Bob
    3PSI gauge
  • bbillcee
    bbillcee Member Posts: 66
    hmmmm so it really doesnt span all that much...thanx
  • BobC
    They are very good vents if you believe you should vent the mains very fast and the radiators slowly. That works for most but not all systems.
    Bob
    3PSI gauge
  • bbillcee
    Bob
    i was looking to use these on the second floor of a 2 story, would they be adequate? was gonna put some gorton #6 and maybe a couple C's
  • Mark N
    Mark N Member Posts: 1,144
    The actual venting rate is based upon system pressure. The higher the pressure the greater the venting rate. What is your system pressure?
  • Abracadabra
    bbillcee said:
    Bob
    Don't use Gorton #6 or Gorton #C on radiators unless you have a seriously long riser. And even then, there's better ways to vent the riser.
  • bbillcee
    bbillcee said:
    Bob
    just going according the manufacturers website suggestions!
  • bbillcee
    i think its a couple pounds i have an WM EG 50 or 55 i forget
  • KC_Jones
    KC_Jones Member Posts: 5,907
    bbillcee said:
    bbillcee said:
    Bob
    I wouldn't....it's generally accepted Gorton makes a great product, but their application recommendations aren't very good.
    2014 Weil Mclain EG-40