vent-rite No 1 adjust vs gorton
bbillcee
Member Posts: 66
on a setting of 1 on the vent rite, what would that roughly equal on gorton? and a setting of 8 would roughly equal what on gorton size?
A Gorton #4 is 0.025, Ventrite at 1 is 0.033, Gorton #5 is 0.080
The Ventrite at 8 is 0.083 about the same as a Gorton #5
3PSI gauge0 -
hmmmm so it really doesnt span all that much...thanx0
They are very good vents if you believe you should vent the mains very fast and the radiators slowly. That works for most but not all systems.
3PSI gauge0 -
i was looking to use these on the second floor of a 2 story, would they be adequate? was gonna put some gorton #6 and maybe a couple C'sBobC said:They are very good vents if you believe you should vent the mains very fast and the radiators slowly. That works for most but not all systems.
Bob
The actual venting rate is based upon system pressure. The higher the pressure the greater the venting rate. What is your system pressure?0
Don't use Gorton #6 or Gorton #C on radiators unless you have a seriously long riser. And even then, there's better ways to vent the riser.bbillcee said:
Bob0 -
just going according the manufacturers website suggestions!Abracadabra said:
Bob
I wouldn't....it's generally accepted Gorton makes a great product, but their application recommendations aren't very good.bbillcee said:
Bob0