New Jacobus vent not closing and spitting water
Jmorgan
Member Posts: 4
I am a first time poster long time reader. I have recently dove into upgrading the ancient radiator vents on my one pipe steam system. I was trying to balance my system as well as fix some broken vents that did not close properly. Reading on this site lead me to replace them with Jacobus orifis style vents.
However after replacing the vents I ran into an awful problem. Now most if not all of my brand new vents do not close and many are whistling and spitting water. I did some more research and it sounded like it could be a pressure issue. I checked the pressure and it goes to 2psi when running which sounds like it should be ok.
Does anyone have any suggestions? This wakes me up every night and is driving me crazy. Could u have gotten a bad batch of vents? Any help is appreciated
It's possible one air valve is faulty but unlikely several are bad. It sounds like your system is running at more than 2 PSI. I use the same vents and they do not make any real noise, you can hear them if it's real quiet but it's not bothersome.
Are you sure it's really only going to 2 PSI? The gauge might be lying, the stock pressure gauge on a boiler do not read pressure at all accurately down at 2 PSI. Check the settings on the pressuretrol, the frond scale should be as low as it can go and the white wheel (behind the front cover) should be set to 1 and lower if it will go there.
There should be a pigtail between the boiler and the pressuretrol, that pigtail can become clogged. The pigtail should be removed and checked to be sure it is clear. While the pressuretrol is off, check the little hole inside the brass mounting fitting to make sure it is clear.
3PSI gauge0 -
Also what size vents did you install on the radiators? How much main venting do you have?0
Please post pics of near boiler piping.0
That boiler is not piped correctly and it's probably making very wet steam. If you have the manual that came with it look at the suggested piping and then look at what you have.
Have you checked the pigtail to make sure it's clear and is the pressuretrol set correctly?
3PSI gauge0 -
Ptrol is set too highknown to beat dead horses0
Set the Main at about 1.5PSI (a bit under the "2" and the differential at about .5PSI (A bit under the "1")
As has been said, the near boiler piping is all wrong. No Header at all. Boiler riser should go innto a Header, Riser(s) to the Main(s) should go after the riser and before the Equalizer and the Equalizer should come off the end of the Header.0 -
Well there's your problem. You need to correct the near boiler piping.Jmorgan said:See photos...im guessing my pressure controller isn't set right... Thoughts?
Adjusting the ptrol helped but it looks like I got some piping to fix