How can we prevent boiler from short cycling?
jimvans
Member Posts: 5
Hi all,
Looking for some extra tips or troubleshooting when it seems that my boiler is short cycling. Thermostat will click on for approximately 3 minutes or so before turning off. We've changed all of the vents on our radiators to vari-vents, which has helped in achieving a more even heating of my 1931 tudor, but I still get a quick on/off out of the thermostat. Thermostat is in a central location, away from other radiators so I'm thinking something my be off with it. Any suggestions?
If it's the thermostat that's clicking on and off -- it's the thermostat. If it's the type with an anticipator, it could be that it is just very badly misadjusted. Otherwise, may I suggest a new thermostat? They're not all that expensive, provided you don't carried away with gadgets and frills...Br. Jamie, osb
Are you sure the thermostat is actually turning off the boiler or is the pressure switch on the boiler doing the switch off? If you turn the t-stat all the way up to max, does the boiler stay on? If not than probably the pressure control on boiler is in charge.
Did you just change out the T-stat?0 -
What kind of thermostat do you have? Is it relatively new? Most come set from the factory with a default setting for forced air (5 cycles per hour) Make sure yours is set for Steam at 1 cycle per hour (2 cycles at most).
I don't believe it is the Pressuretrol as you are not going to build enough pressure in 3 minutes to trip the Pressuretrol. Do you have a Cyclegard Low water Cut Off on that boiler? They will shut the boiler down at specific intervals to check the water level. Safegard LWCO's are probably a better option and don't shut the boiler down.5 -
Thermostat is definitely shutting down the boiler. Have been considering a new thermostat for a while now, so recommendations would be welcome. Unsure of the age of the thermostat, but I've attached a photo. It is a Honeywell thermostat, but I can't tell the model.0
Honeywell makes a good thermostat, just make sure the one you buy has a setting for Steam (1 CPH) hot water (2CPH) and many will have 3, 4 and 5 CPH's as well. Some skip the 2 CPH for some reason and you definitely want that option if you decide you want to try 2 Cycles per hour to even the room temps out a little more than 1 CPH will do. I have the Honeywell 7000 series programable thermostat.1
Do you know what the CPH setting is currently? In the manual go to page 17-18 and make sure you are set to steam heat depending on which one you have you want either function 5 or 6 set to 1. If it is set to anything else that could be the problem. If it is already set to 1 I would be inclined to agree with the above the thermostat has a problem and might need replaced.
https://customer.honeywell.com/resources/techlit/TechLitDocuments/69-0000s/69-2416ES.pdf1 -
Thanks everyone. I just found the manual and went through the settings. Turns out I was at 5CPH. I've now set it to 1CPH. Obviously, I'll have to wait and see how this affects things. Really appreciate the help! I'll report back if this doesn't seem to do the trick.0
That will do the trick!0
You're going to find that works much better on 1 CPH than on 5.
Did the old "round" thermostats have CPH? What is the advantage of CPH?0
On the Honeywell T87 you set the cycle rate by the proper setting of the anticipator. With an electronic thermostat you skip the anticipator and set the cycle rate.0
If you use a Honeywell thermostat and don't set the proper cycle rate you heating system will most likely perform unsatisfactorily. The installation instruction cover how to set it.0
My problem is the CPH causing the boiler to fire and run for 10 minutes, thus running very low supply & return water temps in that 10 minutes. I am worried about condensating due to low temps. Is there any advantage to digital thermostats? Neither Well McLain nor Honeywell has an answer.0
If you get a thermostat, like a Honeywell, you can select the number of cycles from one per hour up to five per hour. Just make sure to read the specs on the thermostat you intend to purchase. Some of them, even some Honeywell models will not have the 2 CPH option programable on them (the model I have, a series 7000 does have 2CPH and it is defined as being for Hot water heat, which it sounds like you may have???)Jimbo said:My problem is the CPH causing the boiler to fire and run for 10 minutes, thus running very low supply & return water temps in that 10 minutes. I am worried about condensating due to low temps. Is there any advantage to digital thermostats? Neither Well McLain nor Honeywell has an answer.
It's been a few days since I changed from my thermostat being at 5 CPH, down to 1. I've seen a huge difference in the way my home heats. Getting to the setting to change this is not very intuitive, but extremely simple once you know how. I'm still considering a new thermostat, as I'd like to have more features. We do not have central air and are considering adding a split-system AC unit in our finished attic. I've seen some compatibility with Honeywell's RedLink system and Mitsubishi split system units, so I'm curious if anyone has any experience with the RedLink thermostats?0
Keep the existing Honeywell you have for your heat. If you put in the AC for other areas, they come with their own thermostats. Let those T-States do their job.
Unless you want to try to make that thermostat do another different job, and avoid a second thermostat, leave the old one alone. It works now. Just remember what a PITA you had until you re-set the CPH setting. Try to make the old Honeywell do two, and you will be resetting the CPH switch twice per year.
Wisely, with a steam system, you are running that T-Stat on "Hold" which over rides the clock feature. Steam systems seem to be happiest when left alone and to run at their own speeds.0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration