Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
What to do with Hoffman 43 Main Vent
Options
STvex
Member Posts: 71
Hi, I had two Hoffman 43's on my main vent. Replaced them with 2 gorton 1's. I have 20 ft to 30 ft of 2 inch main pipe. Now that I have these Hoffmans, what can I do with them? Should I add more connections to the antler and add these hoffmans to the gortons? Waste of time or will I get some added venting? Thanks
0
Comments
-
For 20 to 30 ft of 2" Main, you should have at least the equalivent of 1 Gorton #2 or 3 Gorton #1's. If those Hoffman 43's are still good, you can add them but they don't vent that much air. I'd add about 2 more Gorton #1's.
EDIT: Assuming you have at least a 1/2" tapping for the vent antler.0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 50 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements