Boiler Temp - 100 degrees Fahrenheit
Was the burner firing when you measured the inlet pressure?
The was a question above concerning your gas pipe stop valve.0 -
No I measured the inlet pressure with the burner off. The gascock is straight up and down now, open (it has a broken piece - maybe used to be a handle? - that made it look only partway open). I had to open and close the valve a few times to connect/disconnect the manometer and it seems to be working fine.0
Now measure the inlet pressure again with the boiler off and then fire up the boiler. What does the pressure read with the boiler firing.
3PSI gauge0 -
Okay Bob, I did it. Just now the pressure in the line (boiler off) measured 8.45, so down a bit from earlier. Fired the boiler and the pressure fluctuated quite a bit but never went below 8.00 and never above 8.30.0
Measure that output pressure with the boiler firing again.
3PSI gauge0 -
Why?0
Oh - output pressure. Okay.0
Measured again. .30 to .32 the whole time. Left it connected for about five minutes while boiler was firing.0
If you are on the right port that pressure is 10:1 less than it should be. If it's that low you will never get the heat you should.
Earlier you said the results from clocking the meter was very low, As long as you have the correct pressure at the valve input you should be able to get more pressure out of that valve. That indicates something is not right with the regulator in the gas valve. You should get someone in to look at that valve, it might be defective.
3PSI gauge0 -
What type of manometer do you have?
To be sure of the correct port there is an 1/8" pipe plug in your manifold pipe downstream of your gas valve.0 -
I'm testing the right port. I have the manual and it shows the schematic for the valve - input pressure tap and output pressure tap. You remove the tap plugs with a hex wrench. I am using a Pyle PDMM01 manometer with the barb and tubes that came with it.0
The gas valve manual would give you instructions to raise or lower output pressure. If that has no effect then probably new gas valve time.0