Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Schedule 40 vs. Schedule 80 for Wet Returns
Options
Mike11
Member Posts: 15
We are starting a project where the owner wants to replace the wet returns. Any thoughts on using Schedule 40 or Schedule 80 for a low pressure (less than 2-psig) system. The wet returns are all 2-inch.
0
Comments
-
-
Sorry, no. I should have been more specific. I'm looking to use threaded carbon steel piping.0
-
-
Another option for WET returns is copper. I wouldn't do sch 80 the sch 40 should last beyond the life of the homeowner.1
-
Awesome, confirmed my thoughts on this issue. Thank you!0
-
Schedule 80 is standard procedure for steam condensate piping in commercial and industrial plants. I can't say I have ever seen it used in a house. It will last longer though. The difference in diameter is not enough to be concerned with.0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements
