Confirmation of Radiator EDR
mcvetyty
mcvetyty Member Posts: 50
edited December 2014 in Strictly Steam
Hello,
I am just looking for confirmation that I am calculating EDR correctly. Does the attached radiator have an EDR of 29.26? It is 20 inches tall, and here is the math I used: 11 (sections) x 2.66 (Sq ft/Section).
Thank you!
  • Mark N
    Mark N Member Posts: 1,144
    It's 2.66x11=29.26sq ft EDR
  • mcvetyty
    Ok, perfect. And then I multiply that number by 240 to get the BTUh, is that right?
  • vaporvac
    vaporvac Member Posts: 1,520
    Yes, but if you are looking to replace a boiler, you should base that on the sq ft of steam the boiler makes, NOT its btus. The boiler manufacturer already includes the pick-up factor in their rating. compare apples to apples.
  • Fred
    Fred Member Posts: 8,542
    I looked it up in Dan's EDR book and a six tube, 11 section, 20" tall radiator is 33 sq. ft.
  • mcvetyty
    Thanks Vaporvac, but not looking to replace a boiler. Looking to confirm I need a larger radiator in my kitchen.
    Thanks Fred - 33 sq ft, or 33 EDR?
  • Fred
    The sq. ft. is of EDR. 33 sq. ft. of EDR = 7920 BTU's per hour
  • mcvetyty
    Oh, perfect, and good to know. Last question then - is it normal in this day and age to have radiators that significantly exceed a rooms need, or am I doing something wrong in my calculation?
    For example, I have another room thats radiators BTUh I've calculated to be at 10,800 and this site is stating I require only 4,686!
    http://www.bestheating.com/btu-calculator
  • Fred
    Not unusual. Back when these radiator were installed, with coal fueled boilers, they just simmered all day. Most every house with steam heat has larger radiators than needed but they work well as long as the boiler is matched well to the capacity of the total EDR. On most days those radiators won't get hot all the way across so you really aren't pumping more heat into those rooms than needed and you have the flexibility of slowing them down even more with the radiator vents.
  • Dave0176
    Dave0176 Member Posts: 1,178
    Definitely, when these rads were installed they were sized on worst case scenario 0 degrees and the windows wide open. So yes a lot of these old rads are significantly over size. Venting the air slowly will help the room from overheating.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Spunky424
    Spunky424 Member Posts: 82
    The vent on that radiator seems a bit too high. I would place it in the middle port that looks like it needs to be tapped.