Hoffman Differential system
ScottLichon
Member Posts: 2
I have had the pleasure of being introduced to a Hoffman differential loop system. The first firing of the new boiler, water level steady. Vaporstat set at 12-14 oz. Boiler ran well for hours with all radiators hot.
Next day system is not heating all radiators, and cycling on vaporstat. While the boiler was dropping pressure, the water line disappeared from the glass trips my 1st and 2nd low water cut offs. System is in a vacuum and I am no longer making steam. Once the water level returns to the glass, low water safetys reset, 90 second prepurge, We start making steam again. burner only fires for about 90 seconds before making the vaporstat. Very interesting stuff. Could it be a problem with the Hoffman Loop? I have flushed the wet and dry returns, replaced all cages in the traps. Anyone have experience with this system?
Has boiler been properly skimmed several times?0
As has been said, skimming is the solution. This kind of activity in the sight glass is classic. It ran fine the first day because the water was relavively clean. Oils were on the sides of the boiler block and on the walls of any new pipe. Heat and steam washes it into the water and ultimately, because oil is lighter than water, it lays on the surface of the water. Draining the boiler won't remove it, it will just cling to the sides as the water level drops. Skimming, and probably several times will resolve your problem.0
Does the differential loop trip? It is very sensitive to pressure and i would almost expect it to.
However, it isn't the problem.
Building that much pressure in 90 seconds means that air isn't getting out of the system for some reason...Br. Jamie, osb
I skimmed the boiler 5 times to date. The water is sparkling.
It seems the hoffman may not be tripping.....
My thought is that the inner tube is possibly plugged....
At 10 oz. Itshould be passing steam.
The loop is luke warm at best.0