2 pipe steam drawings, questions re: HW circuit on steam boiler and venting
JudySweetland
Member Posts: 120
Attached drawings are of a Crown boiler and existing steam piping and HW baseboard water pipings and controls.
Do i need a vent on the return main in a different place than shown? The vacuum breaker looks like it only serves the HWH circuit, it that correct? Should i simplify the HWH circuit, or is this set up a good way to pipe for the HWH circuit?
Is the "tank" shown a small hot water receiver, the tank is home made and copper. There are a couple vents on third floor rads (bullet type) which i will remove when new boiler is installed. What other vents if any should be added. Existing steam vent shown on return line coming from HOT OUT connection on brazed plate heat exchanger fails every year, it spews steam and water within 20 minutes of start up. The two pics are hand drawn and colored coded for clarity. The total EDR (used Dan's EDR book) is 665 square feet. Existing boiler is a Crown 299,000 btuh input 245 lbs per hr out. Can anyone identify how the HWH circuit works and clarify venting for me? Thanks. Hope the pics show right side up.
sorry the pics don't show. anychance you could forgo the hW loop for all steam instead, or just start over with the loop?Two-pipe Trane vaporvacuum system; 1466 edr
I opened drawings ok this am. Isn't there a jpeg image u can open directly under the words: tweet, flag, quote, share, email? Weird if not there on what u can see. I will convert to pdf and reattach. Thanks.vaporvac said:sorry the pics don't show. anychance you could forgo the hW loop for all steam instead, or just start over with the loop?
Hopefully these pdf's show up. These are the drawings mentioned above in my original post. Thanks.0
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 107 Geothermal
- 983 Plumbing
- 389 Solar
