steam system not hearing radiators
Have steam boiler that was converted from oil to natural gas, it hasn't been ran in 4 years. Steam worked fine before stopped using it. Did conversion and it seems as if steam isn't making it to radiators, if I pull vent out it will push out after about 45 minutes, at almost no pressure. Changed all vents on radiators and 2 main vents in basement. Any suggestions greatly appreciated.
    Steamhead Member Posts: 18,184
    Is the firing rate correct?
    Did they clean the boiler thoroughly before installing the new conversion burner?
    Consulting
  • morris31607
    morris31607 Member Posts: 6
    Yes it was cleaned and we are running at 150000btus before oil was at 140 It doesn't seem to be building any pressure closed all valves and tried to get ptrol to kick system ran for about an hour and wouldn't shut down.
  • morris31607
    Also it will run until tstat temp is reached, should it sit off on pressure before tstat?
    What were the combustion test results on the gas burner? What make and model are the burner and the boiler?
    Consulting
  • morris31607
    Not sure on comb test boiler is peerless ec03 will have to get Burnet type later when out of work
  • BobC
    BobC Member Posts: 5,538
    Clock the gas meter to check how much gas it is using, this tells you how to do that.
    http://www.aprsupply.com/support/technical-support/checking-firing-rate-(clocking-meter)
    Bob
    3PSI gauge
  • morris31607
    Thanks will check this and let u know in morning