no header and equalizer???
Paul S_3
Member Posts: 1,289
i went on estimate today, it was a leaking steam boiler . boiler must be replaced. radiation equals to 325 sq ft/78,000 btus. i got job going to replace tomorrow morning. question is existing boiler has one 3" inch going strainght up to a 2" inch main, no header no equalizer no hartford loop return just goes straight into boiler return tapping. system is a one pipe gravity return system , correct me if im wrong i think its a parellel flow sytem, at the ends of the 2 mains there is a main vent then it drops down to 1 inch 1/4" , should i pipe like i normally do ?, drop header, and how did it work for the last 20 years? no check valve on return...thanks paul s
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
They were lucky
for the last 20 years...... pipe it according to the instructions and do a drop header, then you'll KNOW it's right.All Steamed Up, Inc.
Consulting0 -
false water line?
also the old and new boilers water lines , when boiler will be cold the water lines do not look like they fully fill the wet return with water......should i just the boiler on blocks or fit a false water line? thanks paul sASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
I'd go with blocks
since that will also reduce the possibility of flood damage to the boiler.All Steamed Up, Inc.
Consulting0
- 87.2K THE MAIN WALL
- 118 Chimneys & Flues
- 113 Geothermal
- 164 Indoor-Air Quality
- 73 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
