no header and equalizer???

Paul S_3
Paul S_3 Member Posts: 1,274
i went on estimate today, it was a leaking steam boiler . boiler must be replaced. radiation equals to 325 sq ft/78,000 btus. i got job going to replace tomorrow morning. question is existing boiler has one  3" inch going strainght up to a 2" inch main, no header no equalizer no hartford loop return just goes straight into boiler return tapping. system is a one pipe gravity return system , correct me if im wrong i think its a parellel flow sytem, at the ends of the 2 mains there is a main vent then it drops down to 1 inch 1/4" , should i pipe like i normally do ?, drop header, and how did it work for the last 20 years? no check valve on return...thanks paul s
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Steamhead
    Steamhead Member Posts: 17,323
    They were lucky

    for the last 20 years...... pipe it according to the instructions and do a drop header, then you'll KNOW it's right. 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Paul S_3
    Paul S_3 Member Posts: 1,274
    false water line?

    also the old and new boilers water lines , when boiler will be cold the water lines do not look like they fully fill the wet return with water......should i just the boiler on blocks or fit a false water line? thanks paul s
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Steamhead
    Steamhead Member Posts: 17,323
    I'd go with blocks

    since that will also reduce the possibility of flood damage to the boiler. 