6 dead 25hp ac comps in 12 years on one system
. My one and only comp ( comp #7) lasted 18 years! We then shut down the system , dismantled everything and installed 5 little systems of 5t each! That was "public money" that bought all of those dead comps!
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,289
    Wow!!
    Sounds like somebody made the same mistake 6 times. What was the cause of the 6 failures?
    Harvey
  • Techman
    Techman Member Posts: 2,143
    edited August 2014
    A few reasons
    Air handler return was 6" off a block wall. That's 10,000cfm. It was a "Hot Deck/ Cold Deck" set up
    System was run low on Freon, could not pump down into undersized receiver.
    Oversized "double suction riser" , capped off one pipe.
    Hot Gas Bypass/Capacity Control set incorrectly. Found that sucker at 4 in the am.Tripping the oil failure safety.
    Gallons of oil in the evap, 40' below rooftop cond unit.
     Plugged evap/cond coils
    Wrong "cage" assembly of TXV.