internal coil cleaner
zepfan
Member Posts: 442
does anyone know of an internal coil cleaner for a dx (r22) system. we replaced a large semi hermetic compressor installed suction, and liquid line driers with removable cores. evacuated the system overnight and am planning to restart the system sometime friday. my concern is that the defective compressor was a bad motor burn, the oil in the defective compressor was coal black color, and black can still be saw through drier core on the inside of the liquid line when the core was opened . we flushed the evaporator and condenser with rx11 before the new compressor was set in place, this is a self contained (no line set to flush). i thought at one time someone made an internal coil cleaner. but i may be mistaken. thanks and good luck to all
Internal cleaning
There is "stuff" on the market but I'm pretty sure it voids any warranty by the comp mfrg. After 24 hrs of run time ,pump down and change the driers again ,and again . Are you using the "HH" cores for acid removal? After you change the F/D cores and the oil tests OK ,got back 1 week later and retest the oil for acid .0 -
Ditto
As Terry said, there is stuff out there, but I won't use it. I will ocassionally use an RX-11 flush if it was a total burnout (smells burnt and test acid from the start), then blow N2 through the system SEVERAL times.
Terry's procedure is dead on and the only way to insure that you are out of the woods.0 -
Just Keep
Changing the dryers every week or so. Easier then changing the compressor.0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 55 Water Quality
- 47 Industry Classes
