Compression tank for an open system??
Tim Schram_2
Member Posts: 17
Hello all,
I need some help. I am trying to straighten out a radiant application where the original installer used non-barrier tubing, but did nothing to prevent corrosion.
The apartment complex has five buildings all done with 8 zones each. I have located zone valves from Taco to place in the oxygen rich side of the system after I seperate the system with a heat exchanger, but I would think that I would need a compression tank on the tubing side of the system as well along with the bronze pump and the open system zone valves.
I realize that this system is not really open, but for corrosion purposes due to oxygen migration it should be treated as such. These buildings are only 8 years old and have gone through an amazing amount of zone valves, pumps, and compression tanks (they last about 18 months, then rot from the inside out) Any suggestions would be helpful
Thanks
Tim
Thanks
Tim
Open system compression tank
You can get tanks for open system they are a lot more expensive, I'm not sure about what's available in the US but here in NZ we have the Pneumatex (Pneumawell)tanks (from Switzerland), They are Blue instead of the red tanks used for a closed system, Size them as you would a closed system.
They are designated as PWD and can take up to 10 bar (150lbs) pressure.
From 50 litres up the bag can be replaced.The water is stored in the bag and is not incontact with the metallic vessel walls,
http://www.stuecklin.ch/v2003/pdf/aquapresso_E.pdf0 -
I need some help
Hello I come from China,and interested in the Pneumawell tanks (from Switzerland you had mentioned, would you give me an Asian regional sales contact or contact for China region will be better?I have a email address( 2389326915@qq.com ).If I can get your help, I feel very honored.0
- 116 Geothermal
