Residual Gas Detection
mmitpw
Member Posts: 2
in Gas Heating
Residential Gas Forced Air Furnace:
Detecting gas at first nozzle/orifice after heating cycle, is this normal operation?
If so, how long after should gas still be/not be detectable?
valve leakage
ok so I found this explanation from honeywell:
https://customer.honeywell.com/resources/Techlit/TechLitDocuments/70-0000s/70-2320.pdf
apparently gas leakage can occur for up to an hour.
So here's what happened:
I smell gas while changing filter.
Call technician to come check.
Finds small leak in pipe connection - problem fixed.
Wife still smells gas, calls utility co.
they find leakage at first burner orifice - get red tagged.
Call technician again - order new valve.
New valve installed - problem fixed.
Wife still smells gas.
I check with cheapy detector - leakage at first burner orifice
Call technician - ordering new replacement for bad new valve
I have a feeling we'll have the same outcome.
So is it safe?
How do I convince my wife that it is?
Any guidance would be appreciated.0 -
Some detectors are
too sensitive as I am sure you read in the Honeywell paper you referenced. I have even seen them register on fresh pipe dope.
Try this mix some soap and water and take a small brush and put some soap at the orifice and see if it bubbles if not then you are safe.
The tech who keeps changing gas valves should do a pressure test with a manometer ("U" gauge) or a digital manometer. This is fool proof and if he or she is trained on gas systems it is a no brainer.0
