FST-200 Boiler Breeching Rumble after conversion to gas
jblum
Member Posts: 13
There is a pronounced rumble in the horizontal breeching of the 200 horsepower FST-200 boiler with IC burner after conversion from #2 oil to natural gas. The boiler and burner are is 20 years old and never rumbled before conversion to gas. Part of the conversion involved installing a stainless steel liner in the vertical masonry chimney. In the boiler room, the breeching was not changed, but it was re-insulated with lighter insulation after removing the old heavy lagging.
I am looking for referral to an specialist who can help.
Jim Blum
Jim Blum
it is early , my first cup of coffee,
is it possible the combustion air requirements have not been met?
for a quick idea where to look?
if the room has an opening like a window or door to the outside
and you open it, during start up and testing ,
your results are different than with the window or door closed ,
Then , there is insufficient combustion air intake , for an example.
Safe0 -
as i have not heard back from you
would you consider calling the mechanical contractor who installed the burner ?
Let them Know that this happened?
Thank You.0 -
If memory serves
the Federal FST boilers run with a slight positive pressure in the firing zone. Check to see that the breech damper is properly set.
What were your combustion test readings?All Steamed Up, Inc.
Consulting0