American Standard boiler
Andrew Rudin
Andrew Rudin Member Posts: 29
What is the model number and Btu input for an American Standard hot water boiler that is 47" long, 65" high and 31" wide?  The ID plate is long gone.
Thanks,
Andy
  • heatpro02920
    heatpro02920 Member Posts: 991
    picture?
    Oil or gas? sounds like oil, for the input/output, just do the math, fire rate and efficiency.
    Steamhead Member Posts: 17,888
    Post a picture of the boiler
    and we can probably ID it.
    Consulting
  • jakofaltrades
    jakofaltrades Member Posts: 6
    Hi Steamhead,
    I am having the same problem. I don't have the plate to this American Standard hot water boiler.
  • RobG
    RobG Member Posts: 1,844
    Hi Steamhead,
    We'll need a little more information than that :/
    jakofaltrades
  • jakofaltrades
    Hi All,
    I have a boiler with the same problem and so I am posting the pictures. Can someone tell me what the BTU are for this boiler? We have it in a small apartment building but the plate with the model number is missing and we don't know the model number or BTU's. The building was built in 1969 and the boiler was manufactured by American Standard. Please let me know if you have any questions, any help with this will be much appreciated.
    Thank you!
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,411
    edited August 2015
    Why do you need to know? Are you replacing the boiler?
  • jakofaltrades
    No, it works fine but it appears we need to know more about the model and the btu's. We are going to add a check valve and it appears that it also needs a CSD 1.
  • jakofaltrades
    The boiler is missing its plate and it would be great if I could get one off the same old model but I don't know the model number so I thought it maybe one of the member's here might know where to look to get the details of this mystery.
  • JStar
    JStar Member Posts: 2,752
    edited August 2015
    My best guess based on the number of burners is 250,000 to 300,000 BTUH input.
    Can you look inside above the burners and count the amount of boiler sections. What size is the chimney pipe?
  • Matt_67
    Matt_67 Member Posts: 309
    i would clock the gas meter. The CSD-1 refers to testing the safety controls per ASME standards - if you are under 400,000 BTUs the state of Michigan requires the testing every three years instead of annually. Is the check valve you mentioned going on the water feed to the boiler? If it is straight water in the boiler a double check with vent similar to a watts 9d is probably what they would use - if there are conditioning chemicals in the boiler then a more pricey RPZ is required.
    JStar
  • jakofaltrades
    Hi JStar, I am not sure how the boiler sections are defined, but I will take a look. I will also measure the diameter and repost tomorrow.
    Thank you
  • jakofaltrades
    Hi Matt,
    We have not been treating the water for boiler with chemicals. If I can definitively determine the BTU's that will be helpful.
    Thank you
    G-2 series I believe. How many cast-iron sections does the boiler have?
    Consulting
  • unclejohn
    unclejohn Member Posts: 1,833
    I think it's closer to 20K per burner.
  • wholesalerbill
    wholesalerbill Member Posts: 20
    Has anyone thought of doing a heat loss for the building? If the boiler was sized properly, this should pretty much tell you what size boiler you have in there.
  • RobG
    Not true, a heatloss should be done, however most boilers are grossly oversized.
    Rich_49
  • STEAM DOCTOR
    null
    Heatloss may have changed since boiler was installed.
  • wholesalerbill
    True & true. At least they'll know what to put in place of the old American Standard with an up to date heat loss.
    Rich_49RobG
