Bonnet capacity
Hello to all
What does bonnet capacity mean.
I have a friend that wants to replace his forced hot air system that says input 100000 btu bonnet capacity 80000 btu
I know it differs from afue but is this an 80% furnace?
Thanks Michael
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,587
    Output
    Bonnet is output
  • charliechicago
    charliechicago Member Posts: 179
    Chimney liner
    So if I replace it with an 80% I don't need a liner?
  • Ironman
    Ironman Member Posts: 7,894
    Not 80%
    That's not an 80% furnace, it's probably 65% at best. Any thing that would have "bonnet capacity" stamped on it is probably at leas 35 years old, maybe much more.
    A new 80% furnace must have a liner installed with it to prevent flue gas condensation. By the time you pay for that, you could have gotten a 95% one and been better off in most cases.
    Also, a heat loss calculation needs to be done as the old furnace is probably way over-sized for the house and a higher efficiency furnace would have more output.
    Bob Boan
  • charliechicago
    Iron man
    Thank u for the response. You are right that it's an old furnace as you can see from the picture. I had been told exactly what u said but I wanted confirmation. Also that's a great idea about a condensing unit. But I'm still wondering what exactly does bonnet capacity actually mean. Thanks mike