extrol chge
Paul_69
Paul_69 Member Posts: 251
can a extrol tank increase in air pressure by itself on system or would someone have to pump air in? i have from time to time found more than 12 psi in tanks when dropping system to 0 psi to check and had to lower them on single or two story homes.
    Steamhead Member Posts: 18,500
    They may have been
    over-charged at the factory and the original installer did not check for proper pressure.
    Consulting
  • Paul_69
    extrol
    always told you can check pressure in extrol if system is dropped to 0 psi. is it better to pull tank off system?
    EBEBRATT-Ed Member Posts: 20,185
    I like
    I like an isolation valve between the expansion tank and the system and a boiler drain between the expansion tank and the isolation valve. You don't want any water pressure on the tanks bladder to influence the air pressure.