Stoppage in a radiant floor line
Heeltee
Member Posts: 20
One of the circuits coming off the supply side of the radiant floor manifold is not allowing water to get thru to the return manifold. What is the best way to clear this circuit? without having to remove the pex tubing . Any ideas / Thanks
dead loop
Did the loop function properly before?
IT may be air bound you need to purge that loop.0 -
purge it ! No luck !0 -
Did the loop
Function before?
Is this a new install?
Could there be a kink in the pex?
What type of radiant?0 -
are their actuators
on the manifold? Could be the valve is stuck in the closed position.Bob "hot rod" Rohr
Manifold Balancing
Is this loop a long loop compared to the others and maybe is the heat loss to this particular area higher than the rest.
Slab application?
Could also be the circulator size?
Manifolds should be balanced based upon the gpm needed which is calculated by the heat loss of the space. Then size the circ accordingly.
Dave H.Dave Holdorf
Taco, Inc
We don't know
What you have unless you can tell us.
This problem could be a multitude of things.
A side from what's been mentioned.
Debris in the system
Frozen loop
Circ issue.
Crazy loop length compared to others.0 -
back feed thru buffer tank.
thought once had same problem hooked garden hose up to buffer tank closed all loops except one at a time , opened valve on return manifold. back feed 60 psi of water threw loop. Ran for 15 minute. did get a little dirt out. loops were never flushed when install guess they should of been.0
- 50 Industry Classes