Stoppage in a radiant floor line
One of the circuits coming off the supply side of the radiant floor manifold is not allowing water to get thru to the return manifold. What is the best way to clear this circuit? without having to remove the pex tubing . Any ideas / Thanks
  • Gordy
    Gordy Posts: 9,546
    dead loop
    Did the loop function properly before?
    IT may be air bound you need to purge that loop.
  • Stoppage in a radiant floor line
    purge it ! No luck !
  • Gordy
    Gordy Posts: 9,546
    Did the loop
    Function before?
    Is this a new install?
    Could there be a kink in the pex?
    What type of radiant?
    hot_rod Posts: 28,493
    are their actuators
    on the manifold? Could be the valve is stuck in the closed position.
  • Dave H_2
    Dave H_2 Posts: 627
    Manifold Balancing
    Is this loop a long loop compared to the others and maybe is the heat loss to this particular area higher than the rest.
    Slab application?
    Could also be the circulator size?
    Manifolds should be balanced based upon the gpm needed which is calculated by the heat loss of the space. Then size the circ accordingly.
    Dave H.
    Dave Holdorf
    Taco, Inc
  • Gordy
    Gordy Posts: 9,546
    We don't know
    What you have unless you can tell us.
    This problem could be a multitude of things.
    A side from what's been mentioned.
    Debris in the system
    Frozen loop
    Circ issue.
    Crazy loop length compared to others.
  • back feed thru buffer tank.
    thought once had same problem hooked garden hose up to buffer tank closed all loops except one at a time , opened valve on return manifold.  back feed 60 psi of water threw loop.  Ran for 15 minute.  did get a little dirt out.  loops were never flushed when install guess they should of been.