Pressuretrol High Limit Adjust?
cdm
cdm Member Posts: 77
Pressuretrol High Limit control
Steam system - Low pressure cut-in looks OK but high pressure cut-out is 2.25 psi (wheel is set at minimum 1 psi.) . Mains have 50% more venting than required. Any way to reset high set-point?
thanks -cd mulford-
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,917
    Cut-in
    What's your cut-in set to? Does it actually cut in at the pressure it's set to?
  • cdm
    Pressurerol High Limit Adjust?
    Do not know what cut-in pressure is. Perssuretrol is set to minimum, and when burner comes on my 0-5 psi gauge reads '0'. Supposedly a pressuretrols minimum setting is 0.5 psi,
    but I have never seen any reading on the gauge.
    cdm
  • Hap_Hazzard
    Cut-in cut-out differential
    If the cut-in is set to 0.5 and the differential is set to 1.0, and it's cutting out at 2.25 and cutting back in at 0, it sounds like the switch is loose. If it's not, then I'd say you need a new Pressuretrol.
    It's possible to recalibrate the Pressuretrol's baseline, so the cut-in pressure actually is what it's set to, but the switch itself is responsible for the differential. If it's set to 1 but it's actually 2.25, that's just a little too far off, and there's no adjustment for that.
  • cdm
    VXT-24, Thanks - I'll bet your right. Maybe its time for a Vaporstat.
    cdm