thermostat
Paul S_3
Paul S_3 Member Posts: 1,297
Hey everyone....I recently replaced a hot water boiler properly sized to the heating load for a 12 family apartment building....previous boiler was controlled via thermostat in basement where no radiation is present and there was comfort issues.....thermostat is in same place with same problem.....system is a two pipe system....I would like some recommendations on what control to use in this situation.....boiler is 245,000 btu....can I run pump continuously and wire a control to shut pump off when outdoor temp gets to a certain temp.....and use a Tekmar control....would like to not use a thermostat.....system is one zone two pipe system thanks Paul s
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Zman
    Zman Member Posts: 7,614
    TRV
    How is it piped?
    It sounds like you cannot add zone valves. You cannot do an aggressive outdoor reset unless you address boiler condensation.
    Would TRVs be possible? TRV, constant circ, outdoor reset and warm weather shoutoff would be slick.
    Carl
    Albert Einstein
  • Paul S_3
    edited December 2013
    Carl
    I replaced boiler also quoted to change system piping because it's a two pipe recently done in copper.....each apartment (12) has a series loop with radiators off each branch circuit so trv's are not feasible...wanted to use constant circulation with wwsd for pump..and..use a Tekmar 256....I can do piping for boiler protection...would a simple bypass with globe valve be enough.....how about 3 way valve with 741 actuating motor?....but 256 seems better on budget.....any advice thanks Paul s
    347-692-4777
    ASMHVACNYC.COM
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,292
    How about
    a TRV zone valve. You can put one in each circuit anywhere in the circuit. Use a constant pressure circulator. You can put an Outdoor line-voltage thermostat in place to shut down the circulator when it gets warm outside. Finally, use a flow switch to turn the boiler on or off.
    Harvey
  • Paul S_3
    reset
    with that setup am i using a outdoor reset control??i cant use a tstat here....paul s
    347-692-4777
    ASMHVACNYC.COM
  • Harvey Ramer
    What
    kind of boiler did you install?
  • Paul S_3
    boiler
    The boiler is a atmospheric 245,000 btu hot water boiler...Paul s
    347-692-4777
    ASMHVACNYC.COM
  • Harvey Ramer
    Is
    it a cast iron boiler or is it a fin-tube?
  • Paul S_3
    boiler
    Cast iron
    347-692-4777
    ASMHVACNYC.COM
  • SWEI
    SWEI Member Posts: 7,342
    I suspect
    That a fire-tube 250k mod/con would have cost less by the time you get all the controls on the CI boiler.
    Use a thermostatic boiler protection valve.  Caleffi, ESBE, and LK Armatur all have options.
  • Harvey Ramer
    With the system
    I described you are probably better off not using an outdoor reset, unless you use a buffer tank and control the tank temp based on outdoor temp.
    If you choose not to use an outdoor reset you will still have to provide boiler protection. Either with a 3-way diverting valve or with primary-secondary piping.
  • Harvey Ramer
    Your flow
    switch should be set to turn on the boiler at approximately 4.4 to 5 GPM. It should be located on the secondary system piping. Your primary loop should have 24 GPM. The boiler should control the primary loop circulator and not allow it to come on till you reach approximately 140º
  • Paul S_3
    boiler protection
    I've been looking at Caleffi's boiler protection valve....which I would like to use on my job....but in the valves literature it shows it piped with some sort of primary secondary piping.....hydro seperator or buffer tank.....can this valve be used with the type of system I have.....standard two pipe with out primary secondary or woulda simple boiler protection bypass line with a globe valve be more feasible....installing a buffer tank is not realistic with budget....thanks Paul s
    347-692-4777
    ASMHVACNYC.COM
  • Harvey Ramer
    I don't
    think the diverting valve will be necessary. Just make sure your primary loop has 24 GPM and use the triple aquastat on the boiler to turn on your primary loop circulator at 140º to 150º You should not see any damaging water temps on your return.
  • Harvey Ramer
    Here is another
    option that will give you everything you want in a nice little package.
    A Tekmar 360 Floating Action Mixing Control, controlling a 2" four-way mixing valve.
  • Paul S_3
    what
    If I cannot get the extra money for a 2 inch primary loop....would I be able to just use the boiler protection valve in these two types of ways? Thanks Paul s
    347-692-4777
    ASMHVACNYC.COM
  • SWEI
    Right-hand diagram will work
    left-hand one will need some kind of hydraulic separation.  The choice between the two depends on flow rates.