Residual heat from boiler and radiator piping
Robert_H
Robert_H Member Posts: 194
With the new system I was planning to put an old cast rad in the basement to supplement the heat. But in sizing it I was wondering how much the boiler and piping are going to contribute to the warmth of the basement. This might be a stupid question but, Could I leave the radiator out and the system would respond to the heat loss through the PEX.  As we have always heated with wood in this house I have no feel for how much residual heat a boiler/piping put out. The basement is just for storage and I have a workshop down there.
House 42k
1st floor 19k
2nd floor 9.7k
Basement 13k
The first floor radiators are all piped through the basement (home run) with 1/2inch fostapex.  About 220 ft total.
The boiler is a Vitodens 200 B2HA-19 running continuous on ODR. Radiators are on TRVs.
Is it worth considering or is it  negligible?
I assume it could be calculated but am not sure where to start.
Thanks
Robert
    Jamie Hall Member Posts: 26,197
    Yes, it can be calculated... but...
    It's not that hard to calculate, actually.  Half inch pipe is more or less 1/8 square feet of radiation equivalent per foot of pipe.  Give or take.  So your 220 feet would be somewhere around say 25 square feet of radiation, equivalent.  Perhaps, at a reasonable home run temp, around 2500 BTU lost.
    Which is trivial.
    So is the heat lost to the area from a modern boiler -- they are designed, no surprise, to put as much of the heat as possible into the circulating water!
    So my suggestion would be to not worry about it and put a decent sized radiator in there with its own TRV.
  • Robert_H
    Thanks
    Thanks Jamie, that makes good sense.