Pressure relief valve
Went downstairs to check my new mod/con's temps and I find my ~10 yr old 60 gallon SuperStor dumping a fairly strong trickle of water onto the floor from the pressure relief valve. I turned off the feed water and cycled the relief lever about 10-15 times and it seems to be holding fine. DHW temp was 140 by the way. Should I just replace the valve? Is this something you've heard of?
  • billtwocase
    billtwocase Member Posts: 2,384
    thermal x tank?
    Have the valve replaced, and check thermal expansion tank, if there is one
  • Stekay
    Stekay Member Posts: 36
    Thanks
    Expansion tank is brand new with new boiler. It hasn't leaked since, but I'm gonna change it out for piece of mind.
  • Zman
    Zman Member Posts: 7,609
    Expansion Tank
    The relief valve on the water heater is for the domestic water and is independent of the the boiler 's water and expansion tank.
    Do you have a domestic water expansion tank?
    You usually need one if your domestic water system has a check valve at the meter.
    Carl
    Albert Einstein
  • Bob Harper
    Bob Harper Member Posts: 1,162
    TXT
    Verify the correct size for your thermal expansion tank. Undersized tank can result in overpressure and discharge.