need help with one pipe steam system,, rookie!
lappy
Member Posts: 9
Hi,,,, two family house, new Williamson steam boiler installed,,,, problem: 2nd floor, bathroom and bedroom both leaking dirty water out of air vent, one baseboard on 1st floor leaking water,, bad water hammer at start up and water bubbling inside all three radiator,, these are all radiators for back rooms of house if that helps, front of house radiators working perfect,,,,, all radiators pitched the right way, all valves open, swapped out rad vents on bad radiators and working vents still shooting water so that's not an issue,,,, when boiler installed o have no main vent in basement, and also only have wet return, no dry return,,, pressure in system is good, 0.5 cut in and cut out at 1 , lowest settings possible,,,, any ideas??? Posting pic of boiler and piping hopefully shows enough info,, please look over and share your expert steam thoughts,, thank you !
Oh, my
looks like a steam boiler installed by someone who's never even seen a steam system, much less worked on one. Page 11 of the installation manual http://www.williamson-thermoflo.com/en/assets/pdf/w-gsa_manual.pdf shows the MINIMUM acceptable near-boiler piping.
Please tell me you haven't paid the installer in full.0 -
not paid in full
From issues ive said along with pics, what issues do u think im looking at?0 -
Oh My x 2
Open the manual and compare the piping….Not rocket science0 -
Not even close
Modern steam boilers must have the near boiler piping done correctly, the old boilers could work with this kind of piping because they had huge steam chests.. Your boiler has no header and no equalizer and that is why the system is misbehaving, call the installer and tell him he has to configure the piping so it looks like the diagram in the installation manual.
Tell him to install a skim port while he is redoing the boiler piping.
3PSI gauge0 -
what a headache
Guys appreciate the advice,,, so assuming this missing pipe work would definitely b causing these issues I've posted? Second, do I need dry return and main vents installed? So post say yes and some say no?0 -
ordering the book
I've been doing tons of research recently, and ordering book,, figured since I bought this house I might as well become very familiar with steam heating...0 -
Dry return/
It depends on what the rest of the piping in the basement looks like. From your description I assume you have a single pipe steam system (one pipe feeds each radiator). Dry returns are common on two pipe systems; either system needs a way to remove air from the pipes; two pipe systems can have air vents or main traps, single pipe systems should have a main vents near the ends of each steam main
There are two types of mains you could have.
A parallel flow system starts high above the boiler and drops gently as it makes it's way around the basement at the end of the main (after the last radiator takeoff) it drops down to the floor into a wet return and back to the boiler - the steam and the condensate both flow in the same direction. If you have more than one steam main be very sure they don't tie together above the new boilers waterline, you old boiler may have had a higher waterline than the new one does
A counterflow main gently slopes up from the boiler as it works around the basement - the stem flows one way and the water flows the other way. You could have one main that is parallel and the other one that is counterflow bat as close to the ceiling as the main above the boiler is that is not likely.
3PSI gauge0 -
As a direct answer,
yes, the bad pipe work around the boiler could be causing a good many, if not most, of your problems, although there may well be other difficulties as well.
It does sound as though you have a one pipe system (the air vents on the radiators!) -- although it is easy to tell -- if there is only pipe to each radiator, that's what you have. One pipe systems are a little more sensitive to bad near boiler piping, but all steam systems are sensitive to pipe pitch, as some steam does condense in the mains and risers. In one pipe systems, the risers and mains and runouts carry all the condensate from the radiators as well as the steam, so it is important that they are pitched correctly. The book will have a very good description of all of this.
I don't see insulation on the piping near the boiler. When you get the near boiler piping straightened out, you should insulate all the pipes which carry steam. It will help a lot.Br. Jamie, osb
- 167 Indoor-Air Quality