converting a two line system to a single line
bmong
Member Posts: 2
in Oil Heating
I got an oil furnace that was only used for a few months. It was a two line system for the oil lines. With an inlet and return line. My oil tank was an single line system. I capped the return line on the oil pump and hooked up my single line into the oil pump. When I started the furnace,it blew out the seal around the shaft of the oil pump.is there something I need to do to convert from a two line to a single line? Any help would be appreciated.
you need to buy a new pump
It will come set up for a single line system.There was an error rendering this rich post.
you should have a pro install
and set up the pump, and test the combustion set up.There was an error rendering this rich post.
oops.......
You forgot to remove the bypass plug. Another unfortunate case of a DIY'er trying to save some money.
Follow hotpipe's recommendation. Your burner may be set to run at a different pressure then what the pump is factory set to. Then of course, properly connected, bled, pump pressure/vacuum test, and a complete combustion test all need to be done. And while he's there, have him clean the unit, new filter, nozzle, etc.There was an error rendering this rich post.
why
was it set up for 2 pipe? Like others said, pump is no good now. Another thought, if you decide to do it yourself, what is the pump pressure set for on your unit? They come set at 100 PSI I would hire a pro0 -
shaft seal kaput @ 10 PSI
you had over 100 PSI...too many specialty tools are involved, don't even attempt to try it unless you are prepared to learn a lot and spend a lot, and I don't mean just a thousand either, that might get you an efficiency tester and a pump pressure gauge only, still have a long, long way to go... and many hours of learning. If your willing to spend two years at a technical college, its do-able...0 -
This really is
A case of false economy. Trying to "hit & hope" that an oil burner will be properly balanced is close to assuming you have the magic formula to win powerball. You can make it run, maybe but Oil is costly. Get the most out of it and your equipment by having the unit set up properly by a pro. You will save money by doing so.0
