back flow preventer on steam boiler
nycpa
nycpa Member Posts: 108
I have a VXT auto water feeder to my weil steam boiler.  Does anyone know if the VXT has a built in backflow preventer in it?  If not, other than the actual backflow prevent er valv, does anything else need to be installed?  Thanks
  • Dave in QCA
    Dave in QCA Member Posts: 1,806
    Depends
    It depends on your locality and what is now being required. A couple years ago I had to install a "testable" double check back flow preventer. It has to be tested each year and a report sent to the water company.
    Dave in Quad Cities, America
    http://grandviewdavenport.com
  • steveray
    steveray Member Posts: 11
    check valve
    you are required to put a swing check valve and a ball valve between the water feed and the boiler . you should also put a union between the feed and the check valve so you can check that it isn't passing in the event of a flooded boiler. A backflow preventer is required between the feed and the potable water source.
  • vaporvac
    vaporvac Member Posts: 1,520
    Manual feed?
    Does one need a back flow preventer with a manual feed?