tekmar 256
I was called on a job to wire a boiler using a tekmar 256....a different heating contractor installed boiler and could not wire customer provided control...I know how to wire it but when you have to put in what type of radiation is being used what do I put in if there's a combination of baseboard and radiant heating.....?....there is no boiler protection loop for low return water temp...thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • SWEI
    SWEI Member Posts: 7,342
    Tekmar curves
    From http://tekmarcontrols.com/images/_literature/e0003_06.pdf
    There is a minimum target temperature setting for the boiler that sets the bottom of the curve.
  • Zman
    Zman Member Posts: 7,609
    256
    Paul,
    The 256 will control the boiler with outdoor reset. You can set the boiler minimum output.
    It is not designed for two temp systems or boiler protection.
    Carl
    Albert Einstein
  • Paul S_3
    Paul S_3 Member Posts: 1,294
    edited November 2013
    256
    I can still use it right?....do they make a control for 2 temp systems? Thanks paul S (in other words what type of control you wouldve used on a application like this)
    347-692-4777
    ASMHVACNYC.COM
  • SWEI
    Two temps
    A 363 will manage two separate reset curves.  They're somewhat pricey.
    I'd probably just add a Taco iSeries-R for the RFH.
  • Paul S_3
    tekmar 256
    How come this control has a room occupied temp setting and a unnoccupied temp setting if it does not actually sense temp....i believe its a parallel heating curve ...can someone explain that? thanks paul s
    347-692-4777
    ASMHVACNYC.COM
  • SWEI
    It's a curve shift
    triggered by an external signal.